Thanks. I'm beginning to think the same. I reached out to the provider of the UFH manifold - Wunda who replied: "The flow temps of 40deg and 33...
Yes. I have. It's 35.2 degrees.
Thank you. Are you able to elaborate. Are you saying that the behaviour we are seeing is expected and that we simply given a bad recommendation...
Correction - the manifold outlet temperature (which we have been told is the minimum setting) is currently 50 degrees. And perhaps related - the...
You guess correctly. It was I think an aluminium overfloor with ultra level it two self levelling compound on top. This was left to dry for 48...
All. As mentioned in another post, I'm having problems with my recently installed under floor heating. I have a general question I hope you can...
Please see my reply over several posts. I was unable to post as a single message for some reason. Thank you.
The outlet temperature from the manifold is now at the minimum of 40 degrees. Is there a way to further control/lower the outlet temperature going...
Before this period things were operating only for a very short period of time, at around 20 deg higher.
Thank you. It's over 27. And, yes I am aware of the maximum. I have an IR heat sensor and I've just checked another UFH zone which is currently...
Thank you. That at least explains it, though it does mean I'm nowhere nearer to resolving whether the LVT should behave as it is in the...
Apologies All. I'm getting "account locked" when I try to upload any images. I don't know why. Perhaps one of you is able to help. Thank you.
Hi All. We have recently had the above floating LVT installed as part of a wider building project (ground floor refurb) which included the...