    POLYFLOR FINESSE EC VINYL TO BE LAID ON TOPOF F BALL F57 CONDUCTIVE ADHESIVE

    Has anyone done this as we are currently screeding the areas, it was just to get an idea of laying the copper earthing strips and how much is recommended etc
    Any info would be greatly appreciated.
     
  2. UVcure

    UVcure Well-Known Member

    481
    338
    63
    it depends it its a small room or large ? the last one i did in Nora rubber, if it was under 60m2 you didn't need one,
    if its EC do they want it earthed?

    as your laying EC then you just need need to do a small strip 150mm under the floor, and bring this to an earthing point by an electrician, put two in just in case,
    if its Static Dissipative then 150mm along the wall the way the rolls are laying, then two either side at 150 from wall, and then at 20m intervals,
    maybe do two earth points
    if its fully conductive then its 150mm in from walls all the way around ,then 600mm grids both ways , again two earthing points

    not sure if i remember right but i think with the EC you cant go up to metal pipe if you have any, you have to cut 50mm away and then lay normal vinyl without the conductive adhesive and then weld
     